Home › Forums › Forum › Global timer event?
Tagged: Timer
Is there a way to execute a timer on a certain page, regardless of the current page, or do I have to duplicate the timer on every page?
No. There is no means to execute a Nextion side timer across HMI pages.
When you change a page you have emptied the old page out of memory to load in the new page. Therefore the timer is not in memory when you want to run it from another page.
You must be logged in to reply to this topic.