    Is there a way to execute a timer on a certain page, regardless of the current page, or do I have to duplicate the timer on every page?

    Patrick Martin
    Keymaster
    Post count: 3

    No. There is no means to execute a Nextion side timer across HMI pages.

    When you change a page you have emptied the old page out of memory to load in the new page. Therefore the timer is not in memory when you want to run it from another page.